Revised NEC 240.87 requirements make mitigation easier to achieve.
Besides wanting to comply with state regulations, managers knew that insurance providers expect equipment to meet minimum design standards, which the NEC provides. They discovered that the code change makes it easier to protect workers and equipment from arc flash hazards.
In 2014, the NEC was revised in multiple areas. Changes to Paragraph 240.87 have made compliance simpler and less expensive. One easy-to-apply device can simplify meeting the new requirements while providing important additional safeguards for people and equipment.
The previous version of the Code
Paragraph 240.87 of the 2011 edition of the NEC, which was titled Non-instantaneous Trip, said that whenever using a circuit breakerwith a rating of 1,200 A or higher (or one that could be adjusted to 1,200 A or higher) that did not have an instantaneous trip function, one of the following was required:
- Zone-selective interlocking
- Differential relaying
- An energy-reducing maintenance switch with local status indicator.
Zone-selective interlocking addresses a shortcoming of selective coordination. It involves interconnecting downstream and upstream circuit breakers: If a short circuit or ground fault occurs on a branch circuit, the breaker feeding it will trip instantaneously, and simultaneously send a signal to the breaker just upstream, telling it to use its time-delay function instead of tripping instantaneously.
This is important because, otherwise, a downstream short or ground fault could draw enough current to cause both breakers to trip instantaneously, killing power to branch circuits other than the one with the fault.
An unfortunate drawback is that an arc flash may not immediately draw enough current to trip either breaker, resulting in personal injury and damage or destruction of equipment.
Differential relaying uses current transformers at the inputs and outputs of the electrical equipment being protected (zones). When a fault occurs, the zone in which the input and output currents do not match is the location of the fault, and the appropriate breaker is tripped. This is complicated and expensive and takes up a fair amount of space.
An energy-reducing maintenance switch manually sets the current pickup lower and the time delay faster, to trip the breaker feeding a panel as fast as possible while someone is working on it. If there is an arc flash, the breaker should trip instantaneously and limit the energy delivered. This reduces the level of PPE required for the panel. The switch must be activated manually before beginning the maintenance activity to provide protection, and deactivated afterward to prevent future nuisance tripping or miscoordination.
The current version of the Code
The 2014 edition of the NEC changed the name of paragraph 240.87 to Arc Energy Reduction and focused more on personnel protection. As explained in the “2014 NEC Handbook,” the change to this section removes the mention of instantaneous tripsetting from the criteria for applying this requirement.
Instead, it is now required where the highest continuous current trip setting in a circuit breaker is rated or can be adjusted to 1,200 A or higher. It allows for two new methods that can make the job of compliance a good deal easier:
- An energy-reducing active arc flash mitigation system
- An approved equivalent means.
An arc flash relay fulfills the mitigation requirement. Using light sensors, it directly detects the light emitted as an arc flash begins and, in as little as 1 ms, sends an instantaneous trip signal to the breaker feeding the affected panel or enclosure. This stops the arc and minimizes the danger by helping reduce the amount of energy released. This can greatly reduce the potential for arc flash injury to personnel and damage to equipment. It may also reduce the level of PPE required to work on the panel.
This Denver-based company discovered that arc flash relays are easy to incorporate into switchgear designs, and easy to retrofit. The biggest challenge has been minor: deciding where in the cabinet to place the light sensors. Managers are happy that installing a relatively inexpensive arc flash relay not only protects people and equipment directly, but also helps bring the facility into compliance with the new revision of NEC 240.87.
The Bottom Line:
- Zone-selective interlocking addresses a shortcoming of selective coordination. It involves interconnecting downstream and upstream circuit breakers.
- In differential relaying, when a fault occurs, the zone in which the input and output currents do not match is the location of the fault, and the appropriate breaker is tripped.
- An arc flash relay fulfills the mitigation requirement cited in NEC 240.87.
KEYWORDS:
Here are some of the articles at www.plantengineering.com, KEYWORD: ARC FLASH that further discuss this topic:
Six strategies to mitigate arc flash incidents
Arc flashes can also wreak financial havoc in the form of fines, lawsuits, and damage to expensive equipment. Given the dangers they pose, arc flash events merit serious attention from engineering professionals.
New solutions address arc flash energy reduction
In order to maintain selective coordination in some applications, an upstream main circuit breaker may be chosen that does not have an instantaneous trip function. In these cases, if the main circuit breaker were to experience a short-circuit condition, it would remain closed for its preset delay time. And the longer it takes to trip, the higher the arc flash risk.
Exploding the misconceptions and myths about arc flash issues
Large arc flashes are rare, but when they happen, they are life-changing events. Your life is forever changed in a split second—less than 1/10 of a second actually—and and it can never be the way it used to be. The way you feel about your self-worth, the way you interact with your wife (or husband) and family may never be the same again.