Using refrigerants
Refrigeration and air conditioning equipment, in the past, has relied on chlorofluorocarbon (CFC) refrigerants to operate. After evidence began mounting that CFCs were harming the earth's ozone layer, their production in the U.S. was banned under the Montreal Protocol, effective December 31, 1995.
02/15/2002
Sections:
Equipment options
Sidebars:
Safe handling of refrigerants
Refrigerants released many months or years ago are suspected of affecting the ozone layer today. Over time, these refrigerants slowly rise to the earth's stratosphere where they react with the ozone layer. When this happens, new chemical compounds form and ozone no longer exists in its original form.
Many refrigerants contain chlorine atoms that are thought to combine with ozone atoms to cause ozone depletion. Most refrigerants in use today are classified as CFCs, hydrochlorofluorocarbons (HCFC), and hydrofluorocarbons (HFC).
CFCs contain chlorine, fluorine, and carbon and are considered the most damaging because they reach the stratosphere intact.
A second group of refrigerants in common use is HCFCs. They contain hydrogen, chlorine, fluorine, and carbon. The hydrogen makes them less stable in the atmosphere. These refrigerants have much less potential for ozone depletion because they tend to break down in the atmosphere. The small amount of chlorine in these compounds is released before it reaches and reacts with ozone. This group is due for phaseout in 2020 and 2030 (depending on the compound) because of the chlorine content.
The third group of refrigerants is HFCs. They contain no chlorine and do not harm the ozone layer.
Other refrigerants are mixtures of some existing refrigerants and are called azeotropes and blends.
Azeotrope refrigerants are blends that are combined in such a manner that they will not separate into their individual components. They are considered a unique refrigerant even when they leak into the atmosphere.
Some blended refrigerants are not azeotropes, they are sometimes referred to as "near azeotropes" or simply as blends. They also are considered a unique refrigerant when they leak into the atmosphere.
As existing supplies of refrigerants become depleted, substitutions must be made. The following tables illustrate which refrigerants and blends will work and what must be done to implement their use.
Plant Engineering magazine extends its appreciation to E.I. DuPont Co., Suva Refrigerants Div. and York International Corp. for their assistance in the preparation of this article.
Equipment options
With the phaseout of CFCs, some decisions have to be made.
Convert to service refrigerants
Service refrigerants, such as R-401A and R-402A, make good sense because they offer proven performance, are easy to use, result in a low-cost retrofit, and will be available longer than the expected service life of most equipment.
They are economical because only 75% to 90% of the CFC charge is required, minimal changes are needed, and retrofitting is simple and easy.
Convert to HFC
Retrofitting to an HFC refrigerant such as R-134a or R-404A is more expensive and involved than retrofitting to a service refrigerant. An HFC retrofit requires conversion to a polyol-ester lubricant and three or more lubricant flushes may be needed. However, HFC refrigerants are not scheduled for phaseout, which could make their use cost-effective in equipment expected to last 20 yr or longer.
Replace the unit
If the future performance of a system is deemed unreliable, total replacement is probably the most cost-effective solution. The difficulty of retrofitting old or malfunctioning equipment might not be worth the cost or effort. An additional bonus of replacing aging units with new equipment designed to use HFC refrigerants is that the new units can achieve improved energy performance.
Keep CFCs until supply runs out
This might be the best option for older units that are running properly and have no significant leakage. Before selecting this option for equipment with a long expected service life, remember the price of CFCs will continue to increase and availability will decline.
Convert to R-22
R-22 is frequently considered as a retrofit choice because it has been in use for years and people are familiar and comfortable with it. Although R-22 is currently inexpensive, total conversion costs are usually higher than converting to a service refrigerant because compressor modification or replacement as well as other equipment changes are often required.
Refrigerant cylinder identification
Refrigerant
Cylinder color
R-11
Orange
R-12
White
R-13
Light blue
R-22
Light green
R-23
Light blue-gray
R-123
Light blue-gray
R-134a
Light blue
R-401A
Pinkish-red (coral)
R-401B
Yellow-brown (mustard)
R-402A
Light brown (sand)
R-402B
Green-brown (olive)
R-404A
Orange
R-407C
Medium brown (brown)
R-408A
Medium purple
R-409A
Medium brown (tan)
R-410A
Rose
R-500
Yellow
R-502
Light purple (lavender)
R-503
Blue-green (aqua)
R-507
Blue-green (teal)
R-508B
No color, tag it
Refrigerant replacement guide
Product
Application
Comments
Source E.I. DuPont Co.
To replace R-12 and R-500 Short term (HCFC)
R-401A
Retrofit R-12 Medium/low temperature ,best above -15 F evap.
Preferred retrofit option for R-12. No oil change in small, close-coupled systems.
R-409A
Retrofit R-12 Medium/low temperature, best above -15 F evap.
Retrofit option for R-12.
R-401B
Retrofit R-500, R-12 Higher capacity for low temp. R-12, best below -15 F evap
A quick, cost-effective retrofit; one oil change. R-12 retrofit where higher capacity is needed at low temperatures. No oil change in small, close-coupled systems.
Long term (HFC) R-134a
New equipment and retrofit R-12. Medium temperatures.
Good option for new equipment. Also retrofit option; best above 20-F evap; less costly option for retrofit.
To replace R-502 Short term (HCFC)
R-402A
All R-502 temperatures
Preferred retrofit option for R-502. One quick oil change for retrofit; higher capacity.
R-408A
Retrofit option for R-502
R-402B
Higher discharge temp./EER
Preferred for systems where higher discharge temp. is desired; mineral oil commonly used.
Long term (HFC) R-404A
Best option for new equipment.
R-507
Also retrofit option; R-402A less costly option for retrofit.
To replace R-13, R-503 ,and R-23 Long term (HFC)
R-508B
New equipment and retrofit Very low temperature applications: -40 to -150 F
One refrigerant replaces three. Used by major OEMs. Easier and more cost effective retrofit than R-23.
To replace R-22 Long term (HFC)
R-407C
Air conditioning and heat pumps
Available today for retrofit and new equipment
R-410A
Only for equipment designed for air conditioning and heat pumps.
High-pressure/high-efficiency refrigerant of the future.
To replace R-11 R-123
Low-pressure chillers.
Modifications may be required.
What to expect after a retrofit (general rule-of-thumb)
Refrigerant
Discharge pressure, PSI
Suction pressure, PSI
Discharge temperature, F
Refrigeration capacity, %
Notes: R-402A, R-402B, R-404A, and R-408A are compared to R-502.
R-134a, R-401A, R-401B, and R-409A are compared to R-12.
R-407C is compared to R-22.Source E.I. DuPont Co.
R-134a
+10
-2
-10
-10
R-401A
+20
Same
+25
+10
R-401B
+30
+2
+30
+15
R-402A
+40
+5
-5
+15
R-402B
+30
+5
+15
+15
R-404A
+20
Same
-10
Same
R-407C
+15
Same
-15
Same
R-408A
+5
Same
+20
+5
R-409A
+25
Same
+30
+10
R-507
+30
Same
-15
Same
Refer to the Material Safety Data Sheet (MSDS) prior to handling and use.
Store refrigerants in a clean, dry area out of direct sunlight. Never heat cylinders above 125 F.
Never pressurize systems or vessels containing refrigerants with air for leak testing or any other purpose.
Never tamper with cylinder valves or pressure relief devices.
Never refill disposable cylinders with anything. Do not use disposable refrigerant cylinders as compressed air tanks.
Wear protective clothing such as gloves and eye protection when handling refrigerants.
Avoid contact with liquid refrigerant, frostbite may occur.
Avoid exposure to vapors from spills or leaks.
Evacuate the area if a large spill occurs. Return only after the area has been properly ventilated.
Do not use handheld leak detectors to check for breathable air.
Verify proper cylinder hookup to system.
Check that the cylinder label matches the color code.
Open cylinder valves slowly.
Avoid rough handling of refrigerant cylinders.
Verify that the system has been completely evacuated with a vacuum pump before cutting any lines.
Before welding or brazing, evacuate the equipment and then break the vacuum with air or nitrogen. Do not perform any repair on pressurized equipment.
Always ventilate the work area before entering and using open flames.