Overcurrent protective devices preserve system integrity
The selection of overcurrent protective devices can have a tremendous impact on the performance of an electrical system. Too often overcurrent protective devices are selected based only on voltage and current ratings. There are many other characteristics of overcurrent protective devices that must be taken into consideration to ensure proper protection of the electrical system.
06/01/2005
Interrupting rating
The National Electrical Code 110.9 requires that equipment intended to break current at fault levels to have an interrupting rating sufficient for the current that must be interrupted. A device's interrupting rating is the maximum amount of short-circuit current at rated voltage that an overcurrent protective device, such as fuses or circuit breakers, can safely interrupt under specific test conditions. Protective devices must be able to withstand the destructive energy of short-circuit currents.
Fault current that exceeds the capability of the protective device may cause the device to rupture violently, causing additional damage to electrical equipment. However, devices with adequate interrupting capability to handle expected fault current are not likely to rupture (See "Comparison of device interrupt ratings").
Overcurrent protective devices have varying interrupting ratings. ANSI Standards for fuses and circuit breakers require the interrupting rating to be marked on the device in most cases. Molded case circuit breakers (MCCBs) that are not marked with an interrupting rating are assumed to have a 5000-A interrupting rating per UL 489, Molded-Case Circuit Breakers, Molded-Case Switches and Circuit-Breaker Enclosures. Common MCCBs often have a 10,000-A interrupting rating. MCCBs with higher interrupting ratings are available, but they must be specified. The available short circuit current must be known to select an MCCB with the proper interrupting rating.
Branch circuit fuses that are not marked with an interrupting are assumed to have a 10,000-A interrupting rating per UL 248, Low-Voltage Fuses. Typical current-limiting fuses, such as Class R, J or L, have interrupting ratings of 200,000 A or 300,000 A. These types of fuses can be applied in nearly any electrical system without concern of exceeding the interrupting rating.
Component protection
Choosing overcurrent protective devices strictly on the basis of voltage, current and interrupting rating alone does not ensure that equipment will not be damaged by short-circuit current. Devices that are not current limiting may not be capable of protecting wire, cable or other components from short-circuit current. The interrupting rating of a protective device pertains only to that device and has absolutely no bearing on its ability to protect connected downstream components.
Quite often, an improperly protected component is completely destroyed under short-circuit conditions while the protective device is opening the faulted circuit. Fuses and circuit breakers must not only be able to safely withstand fault currents, they must also protect the other electrical components of the system.
The NEC states in 110.10 Circuit Impedance and Other Characteristics:
"The overcurrent protective devices, the total impedance, the component short-circuit current ratings and other characteristics of the circuit to be protected shall be selected and coordinated to permit the circuit-protective devices used to clear a fault, to do so without extensive damage to the electrical components of the circuit. This fault shall be assumed to be either between two or more of the circuit conductors or between any circuit conductor and the grounding conductor or enclosing metal raceway. Listed products applied in accordance with their listing shall be considered to meet the requirements of this section."
There are different levels of protection for electrical components as well. Even components that are installed in accordance with the NEC and within their listing and labeling requirements may not be suitable for further use after a fault condition. For example, UL 508, Industrial Control Equipment, includes a short-circuit test-procedure to verify that motor controllers will not be a safety hazard and will not cause a fire. UL 508 tests are for safety with the doors closed, but do allow a significant amount of damage as long as it is contained within the enclosure. UL 508 allows deformation of the enclosure, but the door must not be blown open and it must be possible to open the door after the test.
In the standard short-circuit tests, the contacts must not disintegrate, but welding of the contacts is considered acceptable. Tests allow the overload relay to be damaged with burnout of the current element considered acceptable. For short-circuit ratings in excess of the standard levels listed in UL 508, the damage allowed is even more severe. Welding or complete disintegration of contacts is acceptable and complete burnout of the overload relay is allowed. Therefore, it is not certain that the motor starter will not be damaged just because it has been listed for use with a specific branch circuit protective device.
Protecting branch circuits
There is a method to select a branch circuit protective device that not only provides motor branch circuit protection, but also protects the circuit components from damage. Two documents that offer guidance in evaluating the level of damage likely to occur during a short circuit with various branch circuit protective devices are: Outline of Investigation (UL508E) and IEC (International Electrotechnical Commission) Standard Publication 60947, Low Voltage Switchgear and Control, Part 4-1: Contactors and Motor Starters.
Both documents define two levels of protection for the motor starter:
  • Type 1 — Considerable damage to the contactor and overload relay is acceptable. Replacement of components or a completely new starter may be needed. There must be no discharge of parts beyond the enclosure.
  • Type 2 — No damage is allowed to either the contactor or overload relay. Light contact welding is allowed, but must be easily separable.
    • Motor starter manufacturers must verify that Type 2 protection can be achieved by using a specified protective device. Most manufacturers have both their NEMA and IEC motor controllers verified to meet the Type 2 requirements outlined in UL 508E and IEC 60947-4. Current-limiting devices usually are necessary to provide verified Type 2 protection. In many cases, Class J, Class RK1 or Class CC fuses are required because Class H, Class RK5 fuses and typical circuit breakers do not operate quickly enough under short-circuit conditions to prevent damage to the equipment and still provide Type 2 protection1.
      Short-circuit current ratings
      Short-circuit current rating is not the same as interrupting rating and the two must not be confused. Short-circuit current rating is the maximum short-circuit current a component or equipment can safely withstand when protected by a specific overcurrent protective device or for a specified time. Adequate short-circuit current rating is required per NEC 110.10 (See "What the Code says about short-circuit current rating").
      Equipment and controllers with higher short-circuit current ratings make it easier to specify, install and meet compliance. Also, equipment such as industrial machinery is often moved to other locations. High short-circuit current ratings make it easier to relocate equipment without exceeding the short-circuit current rating requirements at new locations and help to ensure safer installations. Protection with current limiting devices is the easiest and most effective way to achieve higher short-circuit current ratings.
      Selective coordination
      Selective coordination can be defined as isolating an overloaded or faulted circuit from the remainder of the electrical system by having only the nearest upstream overcurrent protective device open (Figs. 1 and 2). This term was actually added to 2005 NEC Article 100 Definitions:
      "Coordination (Selective) Localization of an overcurrent condition to restrict outages to the circuit or equipment affected, accomplished by the choice of overcurrent protective devices and their ratings or settings."
      The 2005 NEC has added requirements for some systems to be selectively coordinated such as Emergency Systems (Article 700), and Legally Required Standby Systems (Article 701). The NEC also requires that elevator circuits be selectively coordinated. The objective of these requirements is to ensure system uptime with the goal of safety of human life during emergencies. Although not required by the NEC, selective coordination is the best practice for all electrical systems, and can be critical to reduce costly downtime. Without selective coordination, a single faulted circuit can shut down an entire facility.
      The design engineer must verify that overcurrent devices are selectively coordinated for the full range of overcurrent that can occur in the system. And the site inspection should verify the overcurrent protective devices are installed as specified to achieve selective coordination. It is possible for both fusible and circuit breaker systems to be selectively coordinated with proper analysis and selection.
      Selective coordination of fusible systems can often be achieved and verified by using selective coordination ratios published by fuse manufacturers. A full short-circuit and coordination study is not necessary to verify selective coordination.
      Selective coordination with circuit breakers depends on their characteristics and settings as well as the circuit parameters for the specific application. Generally, it is difficult to achieve selective coordination with common circuit breakers that incorporate instantaneous trip settings. Circuit breakers with short time-delay settings may be necessary. In some cases, MCCBs or insulated case circuit breakers with a zone interlocking feature are specified with the objective of achieving selective coordination.
      However, these circuit breakers still have an instantaneous trip that overrides the zone selective tripping feature. Therefore, selective coordination may not be achievable for some fault current levels. If circuit breakers are to be considered, a full short-circuit current and coordination study must be done with proper analysis and interpretation.
      Reliability and maintenance
      Perhaps the two most important considerations for achieving successful overcurrent protection are reliability and maintenance. Overcurrent protective devices must operate as specified to ensure the integrity of the electrical system. Mechanical overcurrent protective devices, such as circuit breakers, must be maintained in accordance with manufacturers' instructions and industry standards.
      NEMA AB4, Guidelines for Inspection and Preventive Maintenance of Molded Case Circuit Breakers Used in Commercial and Industrial Applications can provide guidance on proper maintenance and testing requirements. It may be necessary to remove the device from service and test the electrical characteristics in addition to visual inspections.
      If mechanical devices are not maintained, they may not operate as specified, which can compromise the integrity of the electrical system. Lack of maintenance could result in longer clearing times under fault conditions. This can allow extensive damage to electrical equipment as well as creating a greater arc flash hazard (See "Arc flash test sequence").
      Fuses do not have operating mechanisms that would require periodic maintenance. The only maintenance requirement is to ensure the fuse body is not broken or cracked.
      Summary
      There are many characteristics to consider when selecting overcurrent protective devices. Selecting devices based solely on voltage and ampere ratings may not provide adequate protection, and may result in serious misapplications. Overcurrent protective devices must be specified with adequate interrupting ratings in order to safely interrupt short-circuit currents. In addition to being able to safely interrupt fault currents, overcurrent protective devices must be able to protect other electrical components from damage caused by fault currents.
      Often current-limiting overcurrent protective devices are preferred to protect electrical components, allow equipment to attain higher short-circuit current ratings and help to reduce the likelihood or the intensity of an arc flash hazard. Selective coordination is also important to consider in preventing system blackouts. The integrity of the electrical system depends on the overcurrent protective devices operating as specified. Mechanical devices must be properly maintained and operated as intended.
      1 For a listing of Type 2 protection table by motor starter manufacturer visit www.bussmann.com/apen/pubs/
      More Info:
      The author is available to answer questions about this article. Mr. Schomaker can be reached at JSchomaker@CooperBussmann.com . Article edited by Jack Smith, Senior Editor, PLANT ENGINEERING magazine, (630) 288-8783, jsmith@reedbusiness.com
      Further reading
      The Cooper Bussmann SPD Selecting Protective Devices publication can be downloaded from www.bussmann.com . It has an indepth discussion on selective coordination analysis with published fuse selectivity ratios, simple evaluation rules for coordination of instantaneous trip circuit breakers and illustration of short time-delay circuit breakers.
      In these test sequences, eight photographs represent the total time required to clear the applied fault. In the first sequence, the circuit was cleared in 0.1 seconds, or 6 cycles. In the second sequence, the fault was cleared in less than 8.33 ms, or less than
      Test 4 — In this staged test, a circuit breaker with a short time-delay protected the test circuit. The circuit breaker was not a current-limiting protective device. The short time-delay was set to intentionally delay opening for six cycles, or 0.1 second. Unexpectedly, there was an additional fault in the wire way and the resulting blast caused the cover to hit the mannequin in the head. It is important to note the mannequin is not equipped with the proper personal protective equipment.
      Electrical safety is another consideration when choosing overcurrent protection. The electrical industry is currently focusing a lot of attention on electrical safety %%MDASSML%% especially arc flash hazards. Arcing faults can generate tremendous amounts of energy, and pose serious risks to personnel that work on or near electrical equipment. The amount of energy released during an arcing fault depends mostly on the characteristics of the overcurrent protective devices and the available fault current. Therefore, the selection and performance of overcurrent protective devices play a significant role in electrical safety.
      Extensive tests and analysis have shown that the energy released during an arcing fault is related to two characteristics of the overcurrent protective device protecting the affected circuit:
      The time it takes the overcurrent protective device to open %%MDASSML%% The faster the fault is cleared by the overcurrent protective device, the lower the energy released
      The amount of fault current the overcurrent protective device lets through — Current-limiting overcurrent protective devices may reduce the current let-through (when the fault current is within the current-limiting range of the overcurrent protective device) and can reduce the energy released. Lowering the energy released is better for both worker safety and equipment protection.
      Test results
      An ad hoc electrical-safety working-group within the IEEE Petroleum and Chemical Industry Committee conducted tests to investigate arc-fault hazards. These tests and others are detailed in an IEEE paper
      Both tests (Test 4 and Test 3) were identical except for the overcurrent protective device protecting the circuit. In Test 4, a 640-A circuit breaker with a short-time delay is protecting the circuit; the circuit was cleared in 6 cycles. In Test 3, 601-A, current-limiting Class L fuses are protecting the circuit; they opened and thereby interrupted the fault current in less than
      One finding of this IEEE paper is that current-limiting overcurrent protective devices reduce damage and arc-fault energy (provided the fault current is within the current-limiting range).
      Overcurrent protective devices that are not current limiting such as Class H fuses, and standard circuit breakers do not limit the current, and typically take longer to operate under faulted conditions. This can allow more energy to be released during an arcing fault posing a greater electrical hazard. Current-limiting devices such as Class RK1, Class J, and Class L fuses and current-limiting circuit breakers may help to reduce the amount of energy released during an arcing fault and thereby lessen the electrical hazard.
      Staged Tests Increase Awareness of Arc-Fault Hazards in Electrical Equipment IEEE Petroleum and Chemical Industry Conference Record, September 1997, pp. 313-322 (this paper can be found at
      There are several new requirements in the 2005 NEC for equipment to be marked with the appropriate short-circuit current rating. These markings make it easier to verify compliance with NEC 110.10.
      Article 440.4(B) , Air Conditioning and Refrigeration Equipment with Multimotor and Combination Loads — requires the nameplate of this equipment to be marked with its short-circuit current rating. In most commercial and industrial applications, air conditioning and refrigeration equipment with multimotor and combination loads must have the short-circuit current rating marked on the nameplate. Some equipment, such as one and two family dwellings, cord and attachment-plug connected equipment or equipment on a 60 A or less branch circuit are not included in this requirement.
      Article 409.110 , Industrial Control Panels — requires that an industrial control panel be marked with its short-circuit current rating. Article 409 is new in the 2005 version of the NEC.
      Article 670.3(A) ,Industrial Machinery Electrical Panel — requires the industrial machinery control panel nameplate to include its short-circuit current rating. Prior to the 2005 NEC, the machine nameplate had to be marked with only the interrupting rating of the machine overcurrent protective device, if one was furnished. This marking did not represent the short-circuit current rating of the entire machine, but could be misinterpreted as such.
      Article 230.82(3) ,Meter Disconnect Switches (rated up to 600V) — permits a meter disconnect switch ahead of the service disconnecting means, provided the meter disconnect switch has a short-circuit current rating adequate for the available short-circuit current.
      Article 430.8 ,Motor Controllers Component Marking — now requires that motor controllers be marked with their short-circuit current rating. There are some exceptions.