Industrial lighting varies widely by environment and application. From control room to laboratory to warehouse, each has its own lighting requirements. This article describes lamp types and uses, ballast data, and how to specify the proper lighting for industrial areas.
07/06/2001
Plant Engineering - December 2000
LIGHTING
Reference File: Lamp and ballast guide
Sidebar:
HID ballast terminology
Tables:
  • Lighting warehouse areas
  • Fluorescent lamp data
  • IESNA recommended lighting levels
  • HID lamp data
  • Ballast information for HID
  • Ballast information for fluorescent lamps
    • Jack Smith, Senior Editor, PLANT ENGINEERING Magazine
      • Lighting industrial areas
      • Lamp types and uses
      • Ballast data
        • Industrial lighting varies widely by environment and application. Workplaces range from control room to laboratory to warehouse. Each has its own lighting requirements.
          The industrial workplace environment is divided into two general categories—low bay and high bay. Areas where the luminaire is less than 20-ft above the floor are considered low bay, while areas where the luminaire is more than 20-ft above the floor are high bay. Low bay fixtures should spread light and reduce glare, while high bay units should concentrate light with a medium spread and prominent downward light component.
          Luminance — also called brightness — is light emitted from a surface. It is measured in candelas per square meter. Luminance levels should be kept uniform to prevent worker eyestrain and fatigue, which could affect productivity. Also, accidents could occur when moving between areas not uniformly illuminated.
          Lumen output of a lamp at approximately 100 hr of operation is known as initial lumens. The output of a lamp after it has operated for approximately 40% of its rated life is known as mean lumens.
          Color temperature describes the appearance of the lamp source measured in deg Kelvin. High numbers are considered cool and blue in appearance. Low numbers are warm and red/yellow in appearance.
          Color rendering index (CRI) measures on a scale of 1%%MDASSML%%100 how accurately colors appear under a certain source. The most accurate rendering is 100.
          Lamp efficacy is measured in lumens per Watt and is the efficiency of the lamp. Like miles per gallon, the higher the number, the better the energy efficiency.
          Ballasts
          Arc discharge lamps, such as HID and fluorescent, require ballasts to establish the arc and maintain electrical current once the arc is struck. Ballasts also compensate for voltage variations.
          Magnetic and electronic ballasts are available for fluorescent lighting systems. Ongoing developments in both lamps and ballasts are improving their efficiencies and extending their lives. Both translate to cost reductions in your plant.
          The effects of temperature on the life expectancy of a ballast and its components are shown in the accompany graph .
          Typical industrial facility areas
          • Production
          • Inspection
          • Warehouses
          • Offices
          • Public areas
          • Laboratories
          • Clean rooms
          • Control rooms
            • Critical lighting parameters
              • Adequate lighting levels
              • Uniform illuminance
              • Vertical lighting
              • Glare reduction
              • Balance brightness
              • Appropriate color performance
              • Appropriate mounting heights
                • Recommended mounting heights for luminaires are shown in the accompanying illustration .
                  Plant Engineering Magazine extends its appreciation to Philips Lighting and Lithonia Lighting for the use of their material in the preparation of this article.
                  —Jack Smith, Senior Editor, 630-320-7147, jsmith@cahners.com
                  Sidebar:
                  Ballast regulation. Ability of a ballast to control lamp wattage, and therefore lamp output, when subjected to changes in line voltage.
                  Dip tolerance. Amount of line voltage drop a ballast can sustain before the lamp extinguishes. Usually expressed as a percentage; the higher the percentage, the better.
                  Ballast losses. Amount of additional energy a ballast consumes to operate the lamp (line Watts minus lamp Watts). There is usually a tradeoff between ballast losses and ballast regulation.
                  Constant wattage autotransformer (CWA). Lead-type regulator and the most widely used HID ballast. It offers good ballast regulation and moderate ballast losses. CWA is available for metal halide and high-pressure sodium lamps.
                  SCWA. Pulse-start version of the CWA ballast, but with greater lumen capabilities. Use on pulse-start metal halide lamps only.
                  LLRPSL. Low loss reactor used in areas with very little line voltage regulation. They are designed as an energy saving system. Use on pulse-start metal halide lamps only.
                  RLB. Regulated lag ballast (LAG-type regulator, "reg-lag") used in areas where line dip tolerance is critical. It exhibits the best ballast regulation. Use on pulse-start metal halide lamps only.
                  MRB. Magnetic regulated ballast referred to as a regulated or stabilized type, has operating characteristics similar to the RLB. Use on high-pressure sodium sources only.
                  [ Back to top ]
                  Open areasFootcandles on floor
                  Receipt/dispatch
                  Loading bays
                  15
                  Unpacking, sorting,
                  and control station
                  20
                  Packing and dispatch
                  30
                  Supervisor's desk
                  50
                  Open areas
                  Large item storage
                  10
                  Medium item storage
                  20
                  Small item storage
                  30
                  Rack areas
                  Footcandles on racks
                  Manual racks
                  Large item storage
                  10
                  Medium item storage
                  20
                  Small item storage
                  30
                  Self-service racks
                  50
                  Automated racks, high-rise aisles
                  20-50
                  Lamp typeInitial lumensMean lumensLumen depreciationLamp life, 3 hr/startColor rendering index (CRI)Lamp efficacy,
                  F40 T12 Energy saving
                  2650
                  2306
                  0.87
                  20,000
                  60%%MDASSML%%70
                  65
                  F40 T12 Energy saving high color
                  2800
                  2520
                  0.90
                  20,000
                  70%%MDASSML%%80
                  71
                  F32 T8
                  2850
                  2565
                  0.90
                  20,000
                  75
                  86
                  F32 T8 High color
                  2950
                  2655
                  0.90
                  20,000
                  82%%MDASSML%%95
                  89
                  F32 T8 Long life
                  3000
                  2850
                  0.95
                  24,000
                  85
                  95
                  Slimline
                  F48 T12
                  2900
                  2610
                  0.90
                  9000
                  60%%MDASSML%%70
                  54
                  F48 T12 Energy saving
                  2400
                  2160
                  0.90
                  9000
                  62
                  54
                  F96 T12 Energy saving
                  5500
                  4950
                  0.90
                  12,000
                  60%%MDASSML%%70
                  79
                  F96 T8
                  5700
                  5244
                  0.92
                  15,000
                  75
                  98
                  F96 T8 High color
                  5900
                  5369
                  0.91
                  15,000
                  82%%MDASSML%%85
                  100
                  High output
                  F48 T12 HO
                  4050
                  3483
                  0.86
                  12,000
                  60%%MDASSML%%70
                  51
                  Energy saving
                  8000
                  6960
                  0.87
                  12,000
                  60%%MDASSML%%70
                  67
                  F96 T8 HO
                  8200
                  7626
                  0.93
                  18,000
                  75
                  95
                  F numbers refer to wattage, where an F48 lamp is rated at 48 W.
                  Indoor activityAverage fcAverage lux
                  Assembly
                  Simple
                  30
                  300
                  Difficult
                  100
                  1000
                  Exacting
                  300%%MDASSML%%-1000
                  3000%%MDASSML%%10,000
                  Raw material processing (cleaning, cutting, crushing, sorting, grading, etc.)
                  Course
                  10
                  100
                  Medium
                  30
                  300
                  Fine
                  50
                  500
                  Very fine
                  100
                  1000
                  Inspection
                  Simple
                  30
                  300
                  Difficult
                  100
                  1000
                  Exacting
                  300%%MDASSML%%1000
                  Material handling
                  Shipping and receiving
                  30
                  300
                  Wrapping, packing, labeling
                  30
                  300
                  Picking stock and classifying
                  30
                  300
                  Loading (inside truck)
                  10
                  100
                  Machining
                  Rough bench or machine work
                  30
                  300
                  Medium bench or machine work
                  50
                  500
                  Fine bench or machine work
                  300%%MDASSML%%1000
                  Extra-fine bench or machine work
                  300%%MDASSML%%1000
                  Storage rooms or warehouses
                  Inactive
                  5
                  50
                  Active, bulky items, large labels
                  10
                  100
                  Active, small items, small labels
                  30
                  300
                  Cleanrooms
                  Workspace
                  80
                  800
                  Food processing
                  Workroom
                  30
                  300
                  Inspection areas
                  150
                  1500
                  Outdoor activity
                  Average fc, horizontal/vertical
                  Average lux, horizontal/vertical
                  Building exteriors
                  Active entrances
                  5/3
                  50/30
                  Inactive entrances (normally locked)
                  3/3
                  30/30
                  Building surrounds
                  5/3
                  50/30
                  Storage yards
                  Active
                  10/3
                  100/30
                  Inactive
                  1/0.3
                  10/3
                  Building and monuments, floodlighting (vertical only)
                  Bright surroundings, light surface
                  3
                  30
                  Bright surroundings, dark surface
                  0
                  100
                  Dark surroundings, light surface
                  3
                  30
                  Dark surroundings, dark surface
                  3
                  30
                  HID lamp data
                  Nominal lamp wattageInitial lumensMean lumensLamp life, 10 hr/startColor rendering index (CRI)Typical startup, minTypical restrike, minLamp efficiency, means lumens/W
                  Metal halide - clear
                  175
                  14,000
                  12,000
                  10,000
                  65
                  2%%MDASSML%%5
                  10%%MDASSML%%15
                  69
                  250
                  22,000
                  17,000
                  10,000
                  65
                  2%%MDASSML%%5
                  10%%MDASSML%%15
                  68
                  400
                  36,000
                  25,000
                  20,000
                  65
                  2%%MDASSML%%5
                  10%%MDASSML%%15
                  63
                  1000
                  110,000
                  88,000
                  12,000
                  65
                  2%%MDASSML%%5
                  10%%MDASSML%%15
                  88
                  Metal halide - coated
                  175
                  14,000
                  10,000
                  10,000
                  70
                  2%%MDASSML%%5
                  10%%MDASSML%%15
                  57
                  250
                  21,500
                  17,000
                  10,000
                  70
                  2%%MDASSML%%5
                  10%%MDASSML%%15
                  68
                  400
                  36,000
                  25,000
                  20,000
                  70
                  2%%MDASSML%%5
                  10%%MDASSML%%15
                  63
                  1000
                  107,000
                  85,000
                  12,000
                  70
                  2%%MDASSML%%5
                  10%%MDASSML%%15
                  85
                  Metal halide high output - clear
                  400
                  44,000
                  34,000
                  20,000
                  65
                  2%%MDASSML%%5
                  10%%MDASSML%%15
                  85
                  Pulse start metal halide (requires special ballast and ignitor)
                  70
                  5500
                  4070
                  12,000
                  65
                  2
                  3%%MDASSML%%4
                  58
                  100
                  9000
                  6390
                  15,000
                  65
                  2
                  3%%MDASSML%%4
                  64
                  150
                  15,000
                  11,300
                  15,000
                  65
                  2
                  3%%MDASSML%%4
                  75
                  200
                  21,000
                  15,800
                  15,000
                  65
                  2
                  3%%MDASSML%%4
                  79
                  320
                  32,000
                  21,200
                  20,000
                  65
                  2
                  3%%MDASSML%%4
                  66
                  350
                  36,000
                  27,000
                  20,000
                  65
                  2
                  3%%MDASSML%%4
                  77
                  400
                  44,000
                  37,400
                  30,000
                  65
                  2
                  3%%MDASSML%%4
                  94
                  150
                  14,250
                  10,300
                  15,000
                  70
                  2
                  3%%MDASSML%%4
                  69
                  200
                  20,000
                  14,400
                  15,000
                  70
                  2
                  3%%MDASSML%%4
                  72
                  350
                  34,500
                  24,900
                  20,000
                  70
                  2
                  3%%MDASSML%%4
                  71
                  400
                  42,000
                  35,200
                  30,000
                  70
                  2
                  3%%MDASSML%%4
                  88
                  Pulse start metal halide reg-lag (requires special reg-lag ballast and ignitor)
                  250
                  23,750
                  19,000
                  20,000
                  65
                  2
                  3%%MDASSML%%4
                  76
                  400
                  44,000
                  37,400
                  30,000
                  65
                  2
                  3%%MDASSML%%4
                  94
                  250
                  22,600
                  17,500
                  20,000
                  70
                  2
                  3%%MDASSML%%4
                  70
                  400
                  42,000
                  35,200
                  30,000
                  70
                  2
                  3%%MDASSML%%4
                  88
                  High pressure sodium - clear
                  70
                  6400
                  5440
                  24,000
                  20%%MDASSML%%25
                  3%%MDASSML%%4
                  1%%MDASSML%%2
                  78
                  100
                  9500
                  8550
                  24,000
                  20%%MDASSML%%25
                  3%%MDASSML%%4
                  1%%MDASSML%%2
                  86
                  150
                  16,000
                  14,400
                  24,000
                  20%%MDASSML%%25
                  3%%MDASSML%%4
                  1%%MDASSML%%2
                  96
                  200
                  22,000
                  19,600
                  24,000
                  20%%MDASSML%%25
                  3%%MDASSML%%4
                  1%%MDASSML%%2
                  98
                  250
                  28,000
                  25,200
                  24,000
                  20%%MDASSML%%25
                  3%%MDASSML%%4
                  1%%MDASSML%%2
                  101
                  310
                  37,000
                  33,300
                  24,000
                  20%%MDASSML%%25
                  3%%MDASSML%%4
                  1%%MDASSML%%2
                  107
                  350
                  46,500
                  44,000
                  24,000
                  20%%MDASSML%%25
                  3%%MDASSML%%4
                  1%%MDASSML%%2
                  126
                  400
                  50,000
                  45,000
                  24,000
                  20%%MDASSML%%25
                  3%%MDASSML%%4
                  1%%MDASSML%%2
                  113
                  1000
                  140,000
                  126,000
                  24,000
                  20%%MDASSML%%25
                  3%%MDASSML%%4
                  1%%MDASSML%%2
                  126
                  High pressure sodium - coated
                  70
                  5950
                  5058
                  24,000
                  20%%MDASSML%%25
                  3%%MDASSML%%4
                  1%%MDASSML%%2
                  72
                  100
                  8800
                  7920
                  24,000
                  20%%MDASSML%%25
                  3%%MDASSML%%4
                  1%%MDASSML%%2
                  79
                  150
                  15,000
                  13,500
                  24,000
                  20%%MDASSML%%25
                  3%%MDASSML%%4
                  1%%MDASSML%%2
                  90
                  250
                  26,000
                  23,400
                  24,000
                  20%%MDASSML%%25
                  3%%MDASSML%%4
                  1%%MDASSML%%2
                  94
                  400
                  47,500
                  42,750
                  24,000
                  20%%MDASSML%%25
                  3%%MDASSML%%4
                  1%%MDASSML%%2
                  107
                  Ballast typeInput WBallast regulation line voltage/line wattageBallast lossesAverage dip tolerance, %Voltages
                  Metal halide
                  400 W CWA
                  458
                  Medium
                  50
                  120, 208, 240, 277, 347, 480
                  400 W SCWA
                  456
                  Medium
                  50
                  350 W SCWA
                  400
                  Medium
                  40
                  400 W LLRPSL
                  425
                  Low
                  25
                  277
                  350 W LLRPSL
                  375
                  Low
                  25
                  277
                  400 W RLB
                  465
                  High
                  45%%MDASSML%%50
                  250 W RLB
                  298
                  High
                  30
                  175 W RLB
                  220
                  High
                  30
                  400 W CWA
                  457
                  Med%%MDASSML%%high
                  40
                  250 W CWA
                  295
                  Med%%MDASSML%%high
                  30
                  400 W MRB
                  480
                  High
                  45
                  120, 208, 240, 277, 480
                  Lamp typesMagnetic T12, T8Electronic T12, T8
                  Typical lumens/W with T8 lamps (4-ft length)
                  72
                  86
                  Operating frequency
                  60 Hz
                  20%%MDASSML%%25 kHz
                  Causes stroboscopic effect
                  Yes, moderate
                  No
                  Sound rating
                  A%%MDASSML%%D
                  A+
                  Operating temperature ratio
                  Base
                  12% cooler
                  Typical harmonic distortion
                  15%%MDASSML%%30%
                  m20%
                  Allowable line voltage variation the ballast can withstand and still properly operate the lamp