The Three Faces of PID
Although proportional-integral-derivative (PID) controllers dominate the process control landscape, they do have their limitations. PID loops can be difficult to configure properly, their behavior is not easily understood, and when they fail to produce the desired closed-loop performance, they can be difficult to troubleshoot.
Vance VanDoren, Ph.D., P.E.
03/01/2007
Although proportional-integral-derivative (PID) controllers dominate the process control landscape, they do have their limitations. PID loops can be difficult to configure properly, their behavior is not easily understood, and when they fail to produce the desired closed-loop performance, they can be difficult to troubleshoot. Part of the reason is that the three elements of PID control are vastly different and do not naturally interact well. Nonetheless, all three are necessary to successful control when they can be made to work together.
Fortunately, 60 years of practical experience has taught us much about the individual characteristics of PID. Engineers and technicians can learn the attributes of “proportional,” “integral,” and “derivative” actions and how they interact. With that knowledge, they can adjust each as needed to solve problematic control situations.
The earliest controllers were proportional-only, but users quickly identified a major drawback. Proportional controllers tended to quit too soon when attempting to eliminate errors between the process variable and setpoint. This steady-state offset is illustrated in the graphic on page 36. Proportional controllers settle for small, but non-zero errors, leaving the process variable at a value somewhat shy of the setpoint. This problem stems from the way that a proportional controller with a gain of P computes the control effort, which is by multiplying the error by a factor of P . A large gain produces a large control effort, which drives the process variable closer to the setpoint. That reduces the error between the two, which in turn reduces the control effort. Eventually the effort is too small to move the process any farther. No gain value can be large enough to generate a control effort large enough to eliminate the error completely.
Adding integral action
Operators discovered that they could overcome the “droop” resulting from waning proportional action by manually adding bias to the control effort—just enough to raise the process variable up to the setpoint. This exercise became known as resetting the loop.
Automatic reset was introduced to perform that function without operator intervention. It would automatically increase the control effort in proportion to the running total or integral of past errors. That forced the control effort and process variable to continue upwards as long as the error remained positive or downwards as long as the error remained negative. Today, automatic reset is known as integral action , although the gain that determines the strength of the integral action in a PID controller is still sometimes called the reset rate .
A high reset rate causes the controller to generate an aggressive control effort as long as the process variable and setpoint differ. But, unlike proportional action, integral action will continue to grow as long as the error remains non-zero. So if the proportional action starts to create a steady-state offset, the integral action will become more and more aggressive about eliminating it. In fact, integral action is so persistent that it will only give up once the error and steady-state offset have both been eliminated entirely.
Process and advanced control
In this simple example of a generic control loop, a proportional-only controller with a gain of 2 drives a process with a steady-state gain of 3. That is, the controller amplifies the error by a factor of 2 to produce the control effort, and the process multiplies the control effort by a factor of 3 (and adds a few transient oscillations) to produce the process variable. If the setpoint is 70%, the process variable will end up at 60% after the transients die out. The error remains nonzero, yet the controller stops trying to reduce it any further.
Unfortunately, integral action comes with its own problems. If the process happens to be particularly sluggish, it may take a while for the error to disappear even if the controller employs an aggressive integral action. But if an operator sets the reset rate too high, the controller will become so ambitious that it overcompensates for every positive error and creates an even larger error in the negative direction (and vice-versa). The ensuing oscillations in the process variable will continue to grow until the control effort starts to cycle back and forth between 0% and 100%.
This hunting or closed-loop instability can also occur if the process is especially sensitive to control efforts or if the process includes its own integral action (such as when liquid accumulates in a tank). The proportional and derivative actions of a PID controller can also exacerbate hunting, depending on the behavior of the process.
Reset windup
Integral action comes into play in situations where a process has an actuator that is too small to implement an especially large control effort. That can happen, for example, when a burner isn’t large enough to supply sufficient heat, a valve is too small to generate a high enough flow rate, or a pump reaches its maximum speed. The actuator is said to be saturated at some limiting value—either its maximum or minimum output.
When actuator saturation prevents the process variable from rising any further, the controller continues to see positive errors between the setpoint and process variable. The controller’s running total of past errors continues to rise, and the integral action continues to call for an increasingly aggressive control effort. However, the actuator remains stuck at its maximum output, so the process variable can’t get any closer to the setpoint.
Because the actuator is already fully on, this reset windup doesn’t affect the controller’s immediate performance. But, if an operator tries to fix the problem by reducing the setpoint back into the range that the actuator is capable of achieving, the controller will not respond.
This problem stems from the enormous value that the total integrated error will have achieved during the time that the actuator was stuck at 100%. That total will remain very large for a very long time, no matter what the current value of the error happens to be. The integral action will remain very high, and the controller will keep pushing the actuator against its upper limit.
In this example, the operator has tried to increase the setpoint to a value higher than the actuator is capable of achieving. After observing that the controller has been unable to drive the process variable that high, the operator returns the setpoint to a lower value. Note that the controller does not begin to lower its control effort until well after the setpoint has fallen because the integral action has grown very large during the controller's futile attempt to reach the higher setpoint. Instead, the controller continues to call for a maximum control effort even though the error has turned negative. The control effort does not begin to drop until the negative errors following the setpoint change have persisted as long as the positive errors have persisted prior to the setpoint change (more precisely, until the integral of the negative errors reaches the same magnitude as the integral of the positive errors).
Here, the operator has repeated the same sequence of setpoint moves, but this time using a PID controller equipped with reset windup protection. Extra logic added to the PID algorithm shuts off the controller's integrator when the actuator hits its upper limit. The process variable still can't reach the higher setpoint, but the controller's integral action doesn't 'wind up' during the attempt. That allows the controller to respond immediately when the setpoint is lowered.
Fortunately, the error will turn negative if the operator drops the setpoint low enough, so the total integrated error will start to fall. Still, a long series of negative errors will be required to cancel the long series of positive errors that had been accumulating in the controller’s running total. Until that happens, the integral action will remain large enough to continue forcing the actuator fully on, as shown on page 38.
Several solutions have been devised to protect against reset windup. Most involve shutting off the integrator when the actuator saturates, though additional measures are generally necessary to prevent the controller from requesting impossible actuator moves in the first place.
Derivative dilemma
The derivative action of a PID controller can also be a mixed blessing. Derivative action decreases the control effort in proportion to the error’s rate of change, so it can decelerate the descent of a process variable that is approaching the setpoint too rapidly. That, in turn, reduces the likelihood of overshoot and hunting.
However, if the derivative action is particularly aggressive, it can put on the brakes so hard that it causes hunting all by itself. This effect is particularly pronounced in processes that reacts quickly to the controller’s efforts, such as motors and robots.
The derivative action also tends to add a dramatic spike or “kick” to the control effort when the error changes abruptly during a setpoint change. This forces the controller to act immediately without waiting for proportional or integral action to take effect. Compared to a two-term PI controller, a full three-term PID controller can even appear to anticipate the level of effort that will ultimately be required to maintain the process variable at the new setpoint (which is why derivative action was originally known as pre-act ).
While such predictive capability is generally a good thing, dramatic spikes in a control effort can be troublesome in applications that require slow and steady changes in the process variable, such as room temperature control. A blast of hot air following every thermostat adjustment would not only be uncomfortable for the room’s occupants, but hard on the furnace as well.
For such applications, it is advantageous to forgo derivative action altogether or calculate the derivative from the negative of the process variable rather than directly from the error. If the setpoint is constant, the two calculations will be identical. If the setpoint only changes in a stepwise manner, the two will still remain identical except at the instant when each step change is initiated. The negative derivative of the process variable will lack the spike present in the derivative of the error.
Derivative action is also a problem for applications that involve noisy measurements. If the controller’s derivative gain or rate parameter is too high, a large control effort will ensue every time the noise fools the controller into thinking that the process variable has changed. The controller could end up generating a large derivative action even if the actual process variable has already reached its setpoint. Fortunately, it is relatively easy to filter out measurement noise before computing the derivative of the process variable.
Fixes abound
Fortunately, all of these problems have been addressed if not fixed altogether in modern PID controllers. Reset windup protection, calculating derivative action from just the process variable, and noise filtering have all become standard features on most commercial PID controllers. These help control the internal dissonance and use the characteristics of each element to its best advantage.
Loop tuning is the art of selecting appropriate values for the proportional, integral, and derivative gains so as to achieve a rapid response to setpoint and load changes without making the closed loop system unstable. This tuning is arguably the most challenging aspect of configuring a PID controller. Fortunately, innumerable loop-tuning techniques and software packages have been developed to facilitate that chore. Loop tuning manually is still a challenge, but even that is becoming easier.
See “Loop Tuning Fundamentals,” Control Engineering , July 2003; and also “Auto-Tuning Control Using Ziegler-Nichols,” Control Engineering , October 2006.
Vance VanDoren is consulting editor to Control Engineering. Reach him at controleng@msn.com .