Take control of PID tuning
Process control can be open or closed loop. An open loop is one in which there is no feedback to the controlling unit. Actuating a switch and setting a potentiometer are simplified examples of open loop control. Open loop control is essentially a manual operation. Control of a process, such as temperature of an industrial furnace or level in a tank, typically requires closed loop control.
Sections: What is PID? Proportional Integral Derivative Applying PID Error Process lags Anti-reset windup Tuning the control loop TheBottomLine… |
Sidebars: Ethernet expansion highlights PTO meeting Is ZigBee poised for industrial growth? Industrial Ethernet seminar ARC launches Benchmarking Consortium |
Control of a process, such as temperature of an industrial furnace or level in a tank, typically requires closed loop control. The components of closed loop control are the control unit, output device and feedback, which is actually the input to the controller. The process to be controlled is called the process variable (PV). The parameter to which you wish the PV to conform is the setpoint (SP). The difference between the PV and the SP is the error (Er).
The nature of the process must be taken into consideration when control concepts are applied. Many processes would be extremely unstable using on/off control. Those processes benefit from a type of control that is neither on nor off, but somewhere in between — namely, PID control.
Fig 1
What is PID?
PID stands for Proportional, Integral and Derivative. It is a method by which closed-loop process controllers can more closely match the PV with the SP, while maintaining process stability.
Closed loop control uses feedback, or an Er signal, to correct a PV and, hopefully, keep it within an acceptable range of the SP. Unfortunately, feedback implies that a change has already taken place — like steering a car by looking out the back window.
With no control, a process is free to go wherever it pleases, like driving across the salt flats. PID control keeps the process within bounds, like driving on a paved road. Unfortunately, the tighter the control is, the narrower the road. This is good in that it keeps the process in tight control, but like the road, it is easier to go into the ditch. The bottom line? Use the least amount of control possible. Lower PID values that still keep the process in control are inherently more stable.
Proportional
The Proportional function (short for Proportional Gain) is a multiplier applied to the Er signal. The higher the Gain, the more correction is applied.
Some controllers use a value called the Proportional Band, which is the inverse of the Gain, expressed as a percentage. In this case, the smaller the Proportional Band is, the more correction. Unfortunately, some controllers use Proportional Band, but refer to the value as the Gain. If you see the phrase “50% Gain,” watch out!
Proportional Band is defined as the percent of the actual change in the Er we would have needed to produce the actual amount of change in the output as there was in the Er. Let’s say the Er in a process changes by 2 V. If the output changes by 2 V, the Proportional Band is 100%. If the Proportional Band is 200%, the output would change by only 1 V (it would take an Er change of 200% of the actual change to increase the output the same amount, or 2 V). A Proportional Band of 50% would change the output by 4 V, because it would take only a 50% change in the Er to change the output the same as the Er.
Integral
In some cases where the load increases and the PV decreases, the controller gain alone cannot make up the difference. A controller can react to changes in the PV or SP directly, as those parameters are fed into it.
The controller, however, has no direct information on changes in the load. As load changes in a process are much more common than SP changes, this is a significant problem. As the Er increases, the output increases due to the Gain of the controller, which increases the PV. As the PV increases, the Er decreases, which decreases the output, which increases the Er, which increases the PV, which decreases the Er, which…
Before the PV gets high enough to satisfy the increase in load, an equilibrium is reached where no more correction is applied, but the SP and the load have not been satisfied.
The amount of time the Er has been present determines the amount of correction. If the Er has been present for a long time, the controller requires more correction than it is getting.
We need to reset the output of the controller to satisfy the change in the load. The Integral is normally called “Reset” for that reason. If it is called Integral Time or Reset Time it is specified in seconds-per-repeat. This means the amount of time, in seconds, for the Integral function to increase the output signal by an amount equal to the Er amount (or to repeat the Er in the output). The larger the reset time is, the longer the time required to change the output, and the smaller the effect of the Integral function.
Some controllers use the inverse, called either “Integral Gain” or “Reset Rate,” specified in repeats-per-minute. This function determines how many times the Er amount will be added to the output in one minute. In this case a larger value means a larger effect.
Obviously, the units must be known to tune the loop, and like with the Proportional function, some controllers use one method but call it by the other name. The best thing is to look at the mathematics for the controller in question.
Derivative
The Derivative function compensates for the rate of change of the Er. For this reason, it is often called “Rate.” Derivative is expressed in seconds (or minutes), and has only one interpretation: the higher the number, the greater the effect. In many applications it is set to zero.
Derivative or Rate control can be thought of as anticipatory. A value of 5 seconds adds an amount of correction to the output immediately that the Proportional function would have added had it started 5 seconds earlier. Put another way, a 5-second Derivative adds immediately the amount of correction that the Proportional function would have contributed 5 seconds later. In other words, Derivative is correction based on how fast the Er is increasing or decreasing.
Even if the amount of Er is small, if it is changing rapidly, the controller might need to start applying correction sooner to prevent extreme overshoot. Derivative works when the PV is returning to the SP as well as when it is moving away from the SP.
In some applications, such as heating, Gain can be quite high without causing oscillations, but some overshoot is often experienced. If overshoot hinders the process, the Rate function can dampen it out, and allow the SP to be reached quickly. Without Rate, the Gain would have to be reduced to eliminate the overshoot, and the overall response would be slower. Typical values might be between
Applying PID
Error
The “Error” is the difference between the PV or Controlled Variable (CV) and the SP of the controller. The Er can be SP—PV, or it can be PV—SP. When Er=SP—PV, an increase in the PV causes the Er, and subsequently the output, to decrease. Thus are the characteristics of a Reverse Acting controller. In a Direct Acting controller, Er=PV—SP, and when the PV goes up, the Er goes up, and the output is increased (Fig. 1).
SP changes and PV variations affect the Er function the same way. Because the Derivative function is related to rate of change, a bump or step change of the SP could cause an undesirable spike in the Derivative. For this reason, the Derivative is usually applied only to the PV, and not the Er as the Proportional and Integral functions are. This eliminates the SP change from the equation. The rate of change of the Er is the same as the PV from which it is derived. Also, the maximum Gain of the Derivative is usually limited, so that step changes in the PV don’t cause near-infinite reactions.
Fig 3
Process lags
Process lags are inherent in the process. There is lag in a heating element from the time when current flows in the element until the element reaches temperature. There is also a lag from that point until the material being heated starts to increase in temperature (Fig. 2).
A much more difficult lag to tune out is “Dead Time,” or the delay in the feedback signal reaching the controller. One way this can occur is when the temperature-sensing element is placed too far downstream from the heater.
Anti-reset windup
Most controllers have a method to prevent the Integral function from continuing to grow increasingly larger when the output cannot bring the PV into control. “Anti-Reset Windup” prevents the Reset function from getting too large. This can occur when the output is saturated, or at its maximum value for an extended period of time. This saturation condition could be due to a large SP change, external control being applied to the PV or a physical blockage in the flow. If the Integral function were allowed to continue to build during this time, it could grow so large that when the process returns to normal, the PV would overshoot the SP before the Reset would be totally used. Implementing Anti-Reset Windup usually involves disabling the integration of the Er signal in some way during periods of saturation.
Some tuning guidelines suggest finding the Natural Period and Ultimate Gain, then using these numbers to determine starting points for the PID parameters.
To determine the Natural Period of a process, increase the loop Gain to the point where overshoot causes the loop to go into oscillation with constant amplitude and frequency. Natural Period is the time between peaks of this oscillation. Ultimate Gain is the amount of Gain that caused these oscillations (Fig. 3).
Seldom can this actually be done in the real world. But a small step-change in the SP can usually produce enough overshoot to remain safe, yet give enough information to make a reasonable approximation of the starting PID values.
A starting point for tuning might be a Gain of about
If the PID algorithm is executed more often than necessary, the loop can try to respond to excessive system noise (such as waves in a tank in which we are controlling level). To prevent this, set the execution rate to a value which results in running the algorithm about 10 times during the predominate time period of the loop (usually the Natural Period).
TheBottomLine…
Simple processes require simple control.
Some tuning guidelines suggest finding the Natural Period and Ultimate Gain to determine starting points for the PID parameters.
Wendell Rice, Controls Engineer, Parsons Technical Services, has been a controls engineer for more than 25 years. He can be reached at (765) 245-5357 or wendell.rice@parsons.com . Mr. Rice currently is assigned to a project in Newport, IN that provides support for the U. S. Army’s chemical weapon neutralization program. Article edited by Jack Smith, Senior Editor, 630-288-8783, jsmith@reedbusiness.com .
The continuing surge in industrial Ethernet served as the cornerstone for much of the discussions at the Profibus Trade Organization’s annual general assembly in Scottsdale, AZ on Aug. 2—4. Development of guidelines for Profinet’s current fieldbus integration project is expected to be complete by October 2005. Edgar Kuester, Profibus International chairman, said this project involves development of guidelines for mapping models and engineering associated with the integration of Profinet with Profibus PA, AS-i, HART, FOUNDATION fieldbus H1, CC-Link and DeviceNet. Profinet integration guidelines for Profibus were completed in 2002 and for Interbus in May 2005. Kuester added that the fieldbus integration project suits Profinet well, based on the technology’s conformance with IEC 61158 and positioning of Profinet as a universal Ethernet solution for industrial markets.
Wireless mesh networking is expected to make significant inroads in industrial monitoring and control applications, according to a recent study from Venture Development Corp. Shipments of wireless products using mesh networking will grow from $6.1 million in 2004 to $25.1 million in 2007, a growth rate of 60.2%, the report says.
In 2004, ZigBee sales accounted for 8.2% of the dollars spent on wireless mesh networking products, with proprietary counterparts raking in 91.8%. However, the projection for 2007 wireless mesh networking products shows ZigBee sales growing to 27.9%, with proprietary products shrinking to 72.1%. Although proprietary products will still dominate the market, ZigBee will sustain significant growth.
Based on the IEEE 802.15.4 standard, ZigBee is a global specification created by a multi-vendor consortium called the ZigBee Alliance. Whereas 802.15.4 defines the physical and MAC layers of an application, ZigBee defines the network/security layer, application framework and, in some cases, the application profile. ZigBee provides users in specific applications with a simple, low-cost global network that supports a large number of nodes with an extremely low power drain on the battery.
WAGO Corp. will present a free three-day seminar on industrial Ethernet control at its North American headquarters in Germantown, WI on Oct. 10—12.
Attendees will receive an introduction to the WAGO-I/O-SYSTEM hardware, overview of industrial Ethernet components and protocols, hands-on IEC 61131-3 programming session with live demo nodes and review/create web services or applications (such as alarm emails, web pages, etc. from the controller) using the 750-841 Ethernet Programmable Controller. The seminar will discuss a variety of application examples , including applications presented by the attendees.
ARC Advisory Group and a group of approximately 40 process industry manufacturers joined together to launch the Benchmarking Consortium to establish common metrics for benchmarking the performance and practices for automation, control and related maintenance assets and resources. The Consortium has created working groups representing 16 companies, which have already created 18 metrics. Although the initial metrics center on automation and control, the benchmarking boundaries will likely expand to IT infrastructure for automation and other industry sectors.
The immediate goal is to grow the consortium with companies from the oil/gas/refining, chemicals, pulp and paper and life science industries. These companies would share their actual plant data on specific metrics in return for receiving comparable data on the same metric from others in the industry.
Current Working Group participants include Air Products & Chemicals, BASF, BP, Celanese Chemicals, Chevron, Citgo, Cytec, Dow Chemical, DuPont, Eli Lilly, ExxonMobil, Hercules, Lyondell, Rohm and Haas, SASOL, and Weyerhaeuser.
