NFPA 70E urges industry to turn it off or put it on
For more than three years the latest revision of NFPA 70E, “Standard for Electrical Safety in the Workplace,” has delivered a simple message: to work safely on electrical installations, turn off the power. And if you can’t avoid working on energized systems, put on the appropriate personal protective equipment to protect against the hazards of shock and arc flash.
Sounds easy. But for some in the industry, it’s just not happening.
“I would say the large industrial base is accepting the fact that they can help safeguard their employees (through 70E),” said John Luke, safety director for ESCO Group in Marion, IA. But Luke, who delivered some 200 electrical safety training classes in 2006, added that “your smaller contractors, a lot of them are probably not doing it. A lot of people haven’t experienced an arc flash incident. It’s not on their radar screen.”
NFPA 70E-specified safety gear for electrical measurement includes FR clothing, head/eye/ear protection, leather+rubber gloves and test tools rated for the electrical environment.
“It’s an education process,” said Jeff Morris, vice-president for electrical PPE manufacturer W. H. Salisbury & Co. “Fifty to sixty percent of people are aware of it, but they’re not doing it. But from electrical contractors up to Fortune 100 companies, there’s awareness that we’ve got to protect our people who are working on potentially energized equipment. People are now saying I can’t ignore it, and the best thing out there is the 70E standard.”
An OSHA endorsement
NFPA 70E was first developed in 1979, with encouragement from the U.S. Occupational Safety and Health Administration. It was designed as an industry consensus standard for electrical safety, aimed at helping workers meet OSHA safety requirements while complying with the National Electrical Code. Since then, 70E has been expanded and revised six times. The latest 2004 version mandates new steps to avoid the hazards of electric arc flash.
OSHA’s support for 70E is clear. In a letter of interpretation dated Nov. 14, 2006, OSHA’s Edwin G. Foulke, Jr. said “OSHA recommends that employers consult consensus standards such as NFPA 70E-2004 to identify safety measures that can be used to comply with or supplement the requirements of OSHA's standards for preventing or protecting against arc-flash hazards.”
What is arc flash? As described in 70E, “When an electric current passes through air between ungrounded conductors or between ungrounded conductors and grounded conductors, the temperatures can reach 35,000 F. Exposure to these extreme temperatures both burns the skin directly and causes ignition of clothing, which adds to the burn injury. The majority of hospital admissions due to electrical accidents are from arc-flash burns, not from shocks. Each year more than 2,000 people are admitted to burn centers with severe arc-flash burns.”
The damage can be crippling %%MDASSML%% even deadly. While there is no‘typical’ arc flash accident, the costs in worker’s compensation alone can reach multiple millions of dollars, according to Todd Hohn, assistant vice-president for risk control for commercial insurer CNA. Add in lost production, pain and suffering, possible fines and damage to the company’s reputation, and the cost can put a company out of business.
Hohn said as larger firms have come to understand their compliance requirements, some are choosing to subcontract out electrical work they would normally do in house, in order to limit their risk.
Safe work practices up front
So it’s no accident that the 2004 edition of 70E covers safe work practices in Chapter 1, right up front. The new version also adds a formula to calculate the arc flash energy available and determine a‘flash protection boundary’ (calculations that must be performed by a professional engineer).
Inside that boundary, flash protective PPE is required, and 70E includes tables that specify what gear is required to protect workers in five hazard/risk categories. Just as important, 70E re-emphasizes that working on live parts is‘the-last-alternative work practice.’
“OSHA has said for a long time now that you couldn’t work with stuff live unless there was some major compelling reason,” said Joseph V. Sheehan, P.E., NFPA chief engineer and staff liaison to the NFPA 70E committee. “It was never based on convenience. It was never based on economics. It was based on the fact that you would avoid a greater hazard if you shut it off. The simplest thing is to shut it off, lock it off: lockout-tagout. Nobody gets hurt, nobody needs PPE, have a nice day and everybody goes home for dinner.”
But there are times, as OSHA and 70E both acknowledge, when work on live equipment is necessary. According to OSHA, equipment must be de-energized “unless the employer can demonstrate that de-energizing introduces additional or increased hazards or is infeasible due to equipment design or operational limitations.” Examples include circuit testing, as well as work on circuits that form “an integral part of a continuous industrial process.”
When measuring voltage in an energized 480 V environment, a switching hood is required. See NFPA 70E Tables 130.7(C)(9a) and (10) for Category 2* and PPE details.
“OSHA is the shall, and 70E is the how,” said Palmer Hickman, director of safety, codes and standards for the National Joint Apprenticeship and Training Committee (NJATC). A joint program of the National Electrical Contractors Association and the International Brotherhood of Electrical Workers, the NJATC develops the courses used to train the majority of union electricians.
We have a solution
“NFPA 70E steps in and says we have a solution,” Sheehan added. “How to shut it off safely with a lockout-tagout program, and then if you have to work it live, how to dress, how to act and what tools to use. It’s really a very prescriptive standard that deals with a performance requirement.”
Part of that solution is to encourage workers and employers to think again about working with live equipment. Annex J of 70E provides an example of a detailed “Energized Electrical Work Permit” to be filled out by the qualified electricians assigned to do the work, and signed by management. It’s designed to ensure that those responsible understand exactly what they are doing, why the work must be done live, what safe work practices they will follow, what level of flash hazard is present and that necessary PPE is available.
“Because of that permit, it makes everybody think,” said Sheehan. “It’s a last-ditch effort to get everybody to stop and think, do we really need to work this live?”
“For so many years, we just worked it hot,” said a 30-year veteran electrician who works at a California semiconductor factory. “We need to change that, to find ways of working it cold. We found that there were a number of situations, to my surprise, where by taking the time and going through it, we were able to shut down, by either doing off-shift, by coming in at five o’clock in the morning or doing it on a weekend, or asking for a window.”
Not so easy
So why is 70E compliance not universal? Blame a lack of awareness and education, say the experts %%MDASSML%% and a production-focused, can-do tradition among electricians. Top it off with issues as pragmatic as how to properly launder fire retardant clothing, and you have a compliance shortfall.
Though they are dramatic and costly, arc flash accidents are not common. Many professionals have never experienced an arc flash. “Those injuries, you just don’t see them that often. I’ve seen two incidents in 24 years,” said Luke. “That’s in 12 to 15 million hours of work. I think there are so may other things that smaller contractors have to concentrate on.”
NFPA 70E mandates that electrical test tools must be safety rated for the electrical environment. For this three-phase 480 V control panel, this electrical test tool must be rated CAT III or higher.
Luke added that in his view, facility managers should pay more attention to analyzing arc flash risk, then reducing arc flash dangers by engineering them out. Installing fast-trip current protection devices, for example, can dramatically reduce the level of risk. “Say you have available fault current of 22,600 A and an arc flash analysis based on six cycles of clearing time for that device,” he said. “Change that down to half a cycle and you’ve considerably reduced the hazard for the individual working on it.”
“The biggest challenge for most people is to understand the hazard,” said Morris. “What is the risk? It takes time, money and effort to determine what your risk is. Once you’ve done that, the 70E piece becomes much simpler.”
“I think that 70E makes it about as easy as it can be,” said Hickman, “but having said that, it’s not easy. There are no shortcuts. Everyone’s looking for easy answers, but really, there’s none.”
Compliance with OSHA and 70E can even appear to be a competitive disadvantage, Hickman added. “If they try to do the right thing, many times the customer will say‘you’re asking me to shut it down, and you’re asking me to use an energized electrical work permit, where your competition doesn’t bother me with those things.’ Our contractors are trying to do the right thing, but the customer looks at that as a problem. They don’t understand what the hazards are.”
Sheehan said habit and culture are also barriers to compliance, but those old habits are starting to change. “This standard uses the latest technology, but people are not up to speed with technology,” he said. “This document (70E) is changing the culture. The skill of the electrician was to be quick and know his stuff, to know how to balance his tools. Those days are gone. You can’t use your skill as PPE anymore.”
As awareness has grown, so has the demand for training. “We can’t keep up with the requests,” said Sheehan. “Right now it is a training frenzy. In the electrical business, I think 70E is the single hottest issue.” Industry and labor groups like NFPA, the Independent Electrical Contractors, Inc., NECA and IBEW deliver training on 70E, as do insurers like CNA, manufacturers such as Salisbury and Fluke and a host of private training contractors. Up on the roof
Still, there are those pragmatic issues that face managers like Mark Kerney, president of Hill York Service Corp., an HVAC firm based in Fort Lauderdale, FL. His team of 115 HVAC mechanics is trained in 70E; now he must determine what kind of PPE package to provide, and how to convince the mechanics to use it as they test and repair equipment that often must be running for proper diagnosis.
“The issues are the cost of the PPE equipment, because you should have a Category IV meter, and the time involved in the person suiting up before and after using the diagnostic tools they need,” Kerney said. “Then of course the main concern is will the mechanics do it in 90 degree heat on a roof? I get the feeling that most of the mechanics will say‘Hey, I’ve been doing this for years, safely. What’s changed?’ Nothing’s changed. I get the feeling this standard was written for a manufacturing plant.”
Faced with similar issues, ESCO specified flame resistant (FR) clothing as standard wear for all of its electricians. “They look like the jeans and shirt I’ve always worn to work,” said Luke. “If you show up for work and you don’t have your flame-resistant clothing on here, we send you home. It’s not that uncomfortable and it’s not that cumbersome.”
When working on energized voltages lower than 240 V, a face shield or safety glasses can be substituted for the switching hood. However, since this is a three-phase panel, the test tool must be rated CAT III or higher.
“At one time the clothing was pretty hot and heavy, but the clothing has gotten much more lightweight,” said John Masarick, manager of codes, standards and safety for IEC. “But there’s still the situation where, if you’re working in the south on a real hot day, and you need the highest level of protection which may include a hood, it can be pretty warm.”
That laundry issue? Washing a flame resistant garment with the wrong laundry products or contaminating it with other fibers can damage its performance. Workers may resist the hassle of sending clothes to a commercial laundry, even if the employer pays.
“It’s hard to get people to wear PPE,” Salisbury’s Morris said. “When you’re out in your yard mowing or weed whacking you should probably use safety glasses and hearing protection, but how many people do?” Yet Morris sees great hope in the industry’s progress toward compliance with 70E.
“70E is the best thing out there,” he said. “Is it perfect? No. That’s why it goes through a five-year review process. My comment when people complain about something is that you can get involved and participate. The process to me is a good process, so you can’t blame 70E.
“What’s neat now is we’re starting to hear some victories,” Morris said. “They’re harder to get, because they don’t make the news.”
Walt Greenwood researches safety, indoor air quality and basic electrical measurement topics for Fluke. He has more than 30 years experience as a news reporter and professional writer.
PPE recommendations based on NFPA 70E
Note: If test occurs in the proximity (within 4 feet) of an energized environment, then the PPE standards for the energized environment apply.
Hazard/Risk Category 1: &240 V electrical environments
(110/120/208/220 V panels, 0-50 hp motors and drives)
Hazard/Risk Category 2*: 240 %%MDASSML%% 600 V electrical environments
(270/480/600 V electrical panels, MCCs, switchgear, transformers, bus bars, UPS and lighting; 100+ hp motors and drives)
Hazard/Risk Category 3: High voltage environments (1600 A or higher)
(Substations, utility transformers, big facility service entrances)
Reference: NFPA (National Fire Protection Association) Standard 70E Tables 130.7 (c)(9)(a), (c)(10), (c)(11)
The Top Plant program honors outstanding manufacturing facilities in North America. View the 2017 Top Plant.
The Product of the Year program recognizes products newly released in the manufacturing industries.
Each year, a panel of Control Engineering and Plant Engineering editors and industry expert judges select the System Integrator of the Year Award winners in three categories.
SCCR, 2018 Maintenance study, and VFDs in a washdown environment.
Welding ergonomics, 2017 Salary Survey, and surge protection
2017 Top Plant winner, Best practices, Plant Engineering at 70, Top 10 stories of 2017
Product of the Year winners, Pattern recognition, Engineering analytics, Revitalize older pump installations
Control room technology innovation; Practical approaches to corrosion protection; Pipeline regulator revises quality programs
The cloud, mobility, and remote operations; SCADA and contextual mobility; Custom UPS empowering a secure pipeline
Setting internal automation standards
Knowing how and when to use parallel generators
PID controllers, Solar-powered SCADA, Using 80 GHz radar sensors
Annual Salary Survey
Before the calendar turned, 2016 already had the makings of a pivotal year for manufacturing, and for the world.
There were the big events for the year, including the United States as Partner Country at Hannover Messe in April and the 2016 International Manufacturing Technology Show in Chicago in September. There's also the matter of the U.S. presidential elections in November, which promise to shape policy in manufacturing for years to come.
But the year started with global economic turmoil, as a slowdown in Chinese manufacturing triggered a worldwide stock hiccup that sent values plummeting. The continued plunge in world oil prices has resulted in a slowdown in exploration and, by extension, the manufacture of exploration equipment.
Read more: 2015 Salary Survey
Maintenance and reliability tips and best practices from the maintenance and reliability coaches at Allied Reliability Group.
The One Voice for Manufacturing blog reports on federal public policy issues impacting the manufacturing sector. One Voice is a joint effort by the National Tooling and Machining...
The Society for Maintenance and Reliability Professionals an organization devoted...
Join this ongoing discussion of machine guarding topics, including solutions assessments, regulatory compliance, gap analysis...
IMS Research, recently acquired by IHS Inc., is a leading independent supplier of market research and consultancy to the global electronics industry.
Maintenance is not optional in manufacturing. It’s a profit center, driving productivity and uptime while reducing overall repair costs.
The Lachance on CMMS blog is about current maintenance topics. Blogger Paul Lachance is president and chief technology officer for Smartware Group.
The maintenance journey has been a long, slow trek for most manufacturers and has gone from preventive maintenance to predictive maintenance.
This digital report explains how plant engineers and subject matter experts (SME) need support for time series data and its many challenges.
This digital report will explore several aspects of how IIoT will transform manufacturing in the coming years.
Maintenance Manager; California Oils Corp.
Associate, Electrical Engineering; Wood Harbinger
Control Systems Engineer; Robert Bosch Corp.
This course focuses on climate analysis, appropriateness of cooling system selection, and combining cooling systems.
This course will help identify and reveal electrical hazards and identify the solutions to implementing and maintaining a safe work environment.
This course explains how maintaining power and communication systems through emergency power-generation systems is critical.
click me