Avoid hidden dangers when applying 30-cycle-rated transfer switches
By installing current-limiting cable limiters with the transfer switch conductors, electrical designers can achieve selectivity, reduce the risk of arc flash, and protect downstream components.
Ken Box, PE, Cummins Power Generation, Minneapolis
12/12/2011
The National Electrical Code (NEC) provides electrical designers with minimum installation requirements for protecting electrical components against the damaging effects of short-circuit currents. Components such as automatic transfer switches (ATSs) can be subjected to potentially damaging short currents during high fault conditions.
In addition, the NEC provides electrical designers with minimum installation requirements for providing selective coordination between overcurrent protective devices. However, there are system designs that present a dilemma for electrical designers when component protection and selective coordination appear to be mutually unachievable.
Withstand current ratings and transfer switches
The UL standard for safety covering ATS is UL 1008. This standard defines the test requirements for short-circuit and fault closing ratings for transfer switches. A transfer switch must withstand a designated level of fault current until its upstream overcurrent protective device opens, unless an overcurrent protective is integral to the transfer switch.
Along the same lines, NEC 110.10 states that electrical components such as transfer switches shall be protected against extensive damage from short circuits.
110.10 Circuit Impedance and Other Characteristics: The overcurrent protective devices, the total impedance, the component short circuit current ratings, and other characteristics of the circuit to be protected shall be selected and coordinated to permit the circuit-protective devices used to clear a fault to do so without extensive damage to the electrical components of the circuit. This fault shall be assumed to be either between two or more of the circuit conductors or between any circuit conductor and the grounding conductor or enclosing metal raceway. Listed products applied in accordance with their listing shall be considered to meet the requirements of this section.
Since transfer switches are not overcurrent protective devices except where integral protection is provided, they must be protected by upstream overcurrent protective devices that are capable of both safely opening under short-circuit conditions and protecting the downstream transfer switch.
Transfer switch withstand ratings involve two key factors. The first factor is the transfer switch’s ability to safely survive its rated level of fault current. The second factor involves the element of time. How long can the switch safely withstand the fault current until the upstream overcurrent device opens and clears the fault?
The time factor used in the UL 1008 short circuit withstand and close test has historically been three cycles for switches larger than 400 A. These three-cycle withstand ratings served the industry reasonably well for many years because older molded case circuit breakers had slower short-circuit interrupting times. Historically, the older molded case breaker took about three cycles to interrupt short-circuit currents. The UL 1008 standard also allows transfer switch manufacturers the option of testing with specific circuit breakers. Either method of testing is acceptable according to the standard. The specific-breaker method results in transfer switches having higher withstand and close-in ratings (WCR) than when short-circuit tested for a duration of three cycles. The close-in rating is the amount of rms symmetrical current a transfer switch can safely close into and conduct during short-circuit conditions.
Figure 1: The amount of energy released during a 30-cycle interruption is shown in this photo. Courtesy: Cummins Power Generation
Modern molded case circuit breakers with microprocessor trip units open and clear faults in significantly less than three cycles. The faster interrupting time provides higher short-circuit WCR for the transfer switch under short-circuit conditions. Ultimately, the end user benefits because the transfer switch has a higher WCR as the result of being tested with specific circuit breakers.
Prior to 2007, UL 1008-listed transfer switches had to be tested and protected by molded case circuit breakers listed to the UL 489 standard. The duration of the short-circuit test is 1.5 cycles for transfer switches smaller than 400 A, and three cycles for switches larger than 400 A. Molded case circuit breakers listed to the UL 489 standard incorporate instantaneous trip elements that open and clear faults instantaneously at or near the breaker’s maximum interrupting rating. The clearing time of modern, UL 489-listed molded case circuit breakers can be as fast as 20 msec or 1.2 cycles.
Some molded case circuit breakers approach current-limiting status by clearing in a half-cycle or less. When current-limiting fuses are used as the overcurrent protective device, their total clearing time is less than a half-cycle. The current-limiting device’s ability to open and clear the fault faster than it takes for the short circuit to reach its peak value reduces the amount of thermal and mechanical energy unleashed upon downstream components. Consequently, transfer switches protected by current-limiting protective devices have significantly higher withstand and close-in ratings because these overcurrent devices interrupt short circuits in less than a half-cycle (see Table 1).
Table 1: Because current-limiting overcurrent protective devices interrupt circuits in less than a half-cycle, the transfer switches that use them have considerably higher WCR. The table lists typical WCR for several transfer switch capacities. Courtesy: Cummins Power Generation
Using 30-cycle-rated transfer switches
In 2007, UL amended the 1008 standard for short-circuit test criteria. Transfer switches were allowed to be protected with circuit breakers incorporating short time ratings as long as the transfer switch was tested for the longer duration of time, that is, longer than three cycles. Low-voltage power circuit breakers listed to the UL1066 standard can incorporate short time delay settings up to 30 cycles (0.5 sec). Articles 700.27 and 701.18 of the 2008 NEC state that “overcurrent devices shall be selectively coordinated with all supply side overcurrent selective devices.” While it is relatively simple to selectively coordinate overcurrent devices in the short time region, challenges frequently arise in the instantaneous region of the time-current curve (see Figure 2).
Figure 2: Although selectivity withing the short-time region is easily achieves, the instantaneous region of the time-current curve can be problematic for electrical designers. Courtesy: Cummins Power Generation
Transfer switches with extended withstand and close ratings (longer than three cycles) give electrical designers the ability to adjust and coordinate the trip settings for upstream power circuit breakers with downstream circuit breakers incorporating instantaneous trip elements. Unfortunately, the use of short time-rated trip units in low-voltage power circuit breakers can potentially allow fault currents to flow for as long as 30 cycles or 0.5 sec. This results in the need for the designer to evaluate the impact of using short time delays in several additional areas, which include:
  • The impact of the additional duration of current flow on devices and equipment downstream from the ATS
  • The impact of greater arc flash energy in downstream devices and personnel.
Figure 3: This chart enables electrical designers to determine the allowable short-circuit current for insulated copper conductors. It indicates the amount of short-circuit energy that will generate the maximum temperature in a particular cable size. Courtesy: Insulated Cable Engineers Association (ICEA). Used with permission.
Electrical conductors and short-circuit withstand ratings
Figure 3 indicates the amount of short-circuit energy (proportional to I2t) that will generate the maximum temperature in a particular size of cable. According to the chart, 500 kcmil cable can withstand about 39,000 A of fault current for 30 cycles. As many systems have much higher levels of available fault current, it would not be acceptable to protect this cable with a breaker with a 30-cycle time delay setting. The chart also indicates that if the 500 kcmil cable is protected by a device that trips in three electrical cycles, it can withstand considerably more than 100,000 A.
An 800-A ATS is commonly supplied with two 500 kcmil conductors per phase fed from 800-A low-voltage power circuit breakers. The load conductors from the ATS are also commonly sized using two 500 kcmil for each phase and the neutral.
Assume copper conductors in both cases. Also assume 82,000 A rms (symmetrical) of fault current is potentially available at the line side lugs of the transfer switch. We can select an 800-A low-voltage power circuit breaker rated 100 kA interrupting capacity at 480 V. We are using short time delays to achieve selectivity with downstream devices.
Transfer switches and component protection
The short time rating of the power circuit breaker is 85 kA for 30 cycles. Consequently, we must select an ATS capable of carrying the 800 A load and listed to withstand 82,000 A for 30 cycles. The component protection problem occurs at the conductors. Each individual 500-kcmil conductor is capable of withstanding 39,000 A rms symmetrical. Together, the conductors can theoretically withstand 78,000 A.
Figure 4: This illustration shows a potential component protection problem. If one 500-kcmil conductor can withstand 39 kA, theoretically two conductors can withstand 78 kA. However, the 82 kA available at the transfer switch exceeds the capacity of the combined conductors. Courtesy: Cummins Power Generation
However, we have 82,000 A rms symmetrical available at the transfer switch. Consequently, we have not complied with the minimum requirements of NEC 110.10 (see Figure 4). We could alleviate the problem by oversizing the or increasing the size of the switch. Typically, an 800 A transfer switch does not have sufficient space for three sets of conductors per phase. Furthermore, increasing the cost of the switch, oversizing conductors, or increasing the ampacity of the switch doesn’t address the issue of exposing personnel to high levels of short-circuit energy.
One could argue that this example is “splitting hairs” just to prove a point. How many short circuits result in nice, clean interruptions without damage to components? There is always damage after a high-level short circuit (see Figure 5). UL 1008 test procedures don’t require the switch to carry rated load after a fault. Because safety—not performance—is the intent of the UL short-circuit test, the device should not be stressed to its limits.
Figure 5: The transfer switch shown in this photo was subjected to its maximum withstand rating for three cycles. Although this switch passed the test, obviously there is damage. Courtesy: Cummins Power Generation
What purpose did it serve to achieve selectivity when the result required replacing the circuit conductors? The NEC mandates selectivity, component protection, and arc flash protection. Safety is the ultimate issue, not convenience. The amount of energy released during a 30-cycle interruption is shown in Figure 1.
Using current-limiting devices to reduce short-circuit energy
Figure 6: This illustration shows how current-limiting devices minimize let-through current, which reduces the amount of short-circuit energy. Courtesy: Cooper Bussman SPD Handbook
The concept of current limitation is illustrated in Figure 6, where the prospective available fault current is shown in conjunction with the limited let-through current associated when a current-limiting cable limiter clears. The area under the current curve is representative of the amount of short-circuit energy let through prior to interruption of the circuit. Since thermal and magnetic forces are proportional to the square of the current, it is critically important to limit the amount of current to as small a value as possible for protection of downstream components.
Keep in mind that the maximum magnetic forces vary as the square of the peak current, whereas thermal force energy varies as the square of the rms current. Current-limiting cable limiter devices can clear short circuits before they reach their maximum possible peak current.
Figure 7: This illustration indicates that the cable limiters installed at this transfer switch potentially see 92 kA short-circuit current. However, the fault current is divided in half because there are two cable limiters. Courtesy: Cooper Bussman
In Figure 7, note that the cable limiters installed at the transfer switch are subjected to the prospective 92,000-A rms symmetrical short-circuit current. Because there are two cable limiters, the fault current is divided in half. In other words, each limiter sees 41,000 A. Because the cable limiters are current-limiting devices and will clear fault levels of this magnitude in less than a half-cycle, the resulting let-through current for each limiter is approximately 14 kA rms and 35 kA peak. The resulting effect is that potentially damaging thermal and mechanical energy is reduced by more than 65%. The reduced let-through energy resulting from the cable limiter’s clearing of the short circuit protects the conductor and transfer switch from high levels of short-circuit damage.
Recommendations
Regarding transfer switches, to achieve selectivity, reduce the arc flash hazard to personnel, and protect downstream components, consider the following recommendations:
  • Analyze and compare the conductor withstand ratings, the transfer switch WCR, and the ANSI breaker short-time rating against the available fault current at the transfer switch
  • Ensure transfer switches and their conductors can survive the duration of the fault based on the listed ratings of the devices
  • Reduce fault current and arc flash energy levels by installing current-limiting cable limiters with the transfer switch conductors
  • Reduce arc flash energy levels by using arc-reducing maintenance switches upstream on the normal and emergency sides of the transfer switch
  • Locate transfer switches close to the loads that they serve. When possible, avoid feeding transfer switches directly from large-ampacity power circuit breakers. This recommendation makes the overall system more reliable, because it would be less likely that a fault on one load will interrupt power to other loads on the system.
Box is a power systems territory sales manager, Cummins Power Generation. He provides application engineering support for power generation products to customers in the healthcare, wastewater, and data center markets. Based in Atlanta, he has more than 30 years of experience in electrical power generation. Box is a published author, an active IEEE member, and a licensed professional engineer.